Two columns 50 cm x 50 cm and 60 cm x 60 cm carry 80 tonnes and 120 tonnes of loads respectively. The centre to centre distance between columns is 5.00 metres. The permissible bearing capacity of the soil is 20 t/m2. If the footing is not to project more than 25 cm beyond the outside of the smaller column, pick up the correct design parameters of the footing from the following:
Options
A. distance of C.G. of the loads from the smaller column = 3.00 m
B. the length of the foundation slab = 7.00 m
C. area of footing slab = 11.00 m2
D. width of the footing = 1.57 m.
E. all the above.
Correct Answer
all the above.